101010 said:When installing a 300 amp 277/480 3 phase service does this require a ct cabinet?
And if not are the meter pans supplied by poco?
This is true, but not every PoCo has a meter botique at their disposal. They try to standardize a little bit, and get the meter inventory pared down to "a few sizes fits all" situation. Best to check w/the PoCo, for sure, but I'd almost bet they're going to want to CT meter that. I've seen direct metering of 480 at 400 amps, but not very often.Designer69 said:there are 400 amp meters and sockets available. You provide the socket poco provides meter.
Ours apparently does; they provide meter bases, even multiple-meter ones. I've never bought a meter base.mdshunk said:This is true, but not every PoCo has a meter botique at their disposal.