300 amp residential

Status
Not open for further replies.

jonesjax

Member
customer wants a 300 amp serv with a sub feed for the 200 amp panel and a 100 amp breaker for an outside panel next to tyhe service. I have been on the phone with Graybar elec and Murry today and no one has bothered top cal me back

Anyone know of a meter combo that would fit this application
 
I have never done a 300 amp service -- either 200 or 400. I would bet that it will be easier to get a 400 and probably cheaper than special ordering a 300 amp unit.
 
Around here we install 300 amp residential services because the POCO will allow the use of a 300 amp meter pan. 400 amps generally require CT's. Also you will need to group your service disconnects together. My guess is that you'll need a 300 amp meter pan and 2 disconnects. One for each panel.
 
I have a SQ-D metermain (combination service entrance device) at my house, it's 400A rated. I have three branch breakers, a 200A, a 150A and a 60A for the pool panel......
 
Check out Milbank, I generally install a 320 amp service, with twin 200 amp breakers, but i'm sure you can get whatever you can imagine... FYI, my POCO has approved certain meter cans I can install, so check with your local POCO before buying anything...
 
Dave_PE said:
I have a SQ-D metermain (combination service entrance device) at my house, it's 400A rated. I have three branch breakers, a 200A, a 150A and a 60A for the pool panel......


dave, where did you get this 400a combo unit, and do you have a pic of it? i heard that square d had come out w/ a 400a version of the cm200s w/ parallel 200's but i can't find a pic of what it looks like. i'm interested in this because it seems easier to use than having to punch 2" ko's in a 400a meter an attach qo2's, which would save me a lot of time. thanks for any info. btw, do you know what you paid for it? supply house here looked it up at the desk and told me $550. seems kinda steep considering the 200a version cost me only $90.
 
http://www.squared.com/us/products/load_centers.nsf/unid/C12DEBCCD50D494585256A70006BC91D/$file/all_in_one.htm

all_in_one.jpg


All-in-One devices provide installation labor savings and have been designed specifically for areas where local codes allow main breaker load centers to be mounted outdoors. All-in-Ones are surface, semi-flush, and convertible (surface/semi-flush) mount designs.
  • Ring or ringless styles available
  • Available in two styles for either QO? or Homeline? interiors
  • 100 A to 400 A Main Ampere ratings
  • Available in 10 to 40 branch circuit space configurations
    semi-flush
  • Generator Kits available to provide switching method between main utility service and back-up power source
  • Can accommodate plug-on SURGEBREAKER™ Secondary Surge Arrester
  • All units built per ANSI C12.7, NEMA PB-1, UL standards 50, 67 and 414 and are listed in UL file number E-6294
  • Devices meet Federal Specifications W-P-115C for government housing
    Devices meet the Electric Utility Service Equipment Requirements Committee (EUSERC) standards
  • NOTE: Check with local utility to ensure selected equipment meets local requirements

Is this it?
 
Although the 400 amp combo unit takes up less space and is less labor intensive, I have never been a fan of them. I still use a 325 amp meter base with 2 200 amp panels on either side. Usually a feed thru panel is what I would use. I would then feed 2 200 amp main lug panels in the house and still have some circuits outside for a pool, a/c, detached garage, etc.
 