I have a location that wants a 800 Amp 120/208v of current 480v gear.
They have drawn up and requested a 480V 350Amp breaker to feed 300KVA transformer feeding a main lug 800-Amp panel.
They didnt account for 125%
Calculated at 350A 480V primary i get a KVA of 290.976, that gives me a 807.69 Amp on secondary, can this still feed a 800-amp main lug panel or do i need 800-amp main breaker to protect the buss,
feeders are listed as parallel 500 MCM 90*C for 430 amps
Thanks in advance