Re: 300 KVA XFMR, Disconnect?
Hello Tryinghard,
Perhaps I can clear up your problem. I understand that the xformer is customer owned and is located outdoors and supplies a building. I assume that the xformer is supplied from the utility source, therefore, it is a service and a service disconnect and overload protection is required at the terminating end of the service conductors. This will be the overcurrent protection of the xformer.
The size of the overcurrent device is based on Art. 450, however the conductors on the primary if there are any are service conductors and must be protected in accordance with Art. 230-90. The secondary conductors must also be protected by OCD sized in accordance with Art.240 tap rules for transformers.
Primary current is 361 amps. 1.25 x 361 = 451; next std size is 500A. I recommend 450 amps for the xformer. Conductors on the load-side of the service disconnect are feeders and must have an ampacity of 450A or more. The specs call for a 1000 amp disconnect switch on the secondary, however, since I assume the secondary conductors are outdoors, Section 240-21(C)can be used. If 1000 amps of OCP is used, the secondary conductors must have an ampacity of 1000 amps.
Section 225-31 thru 225-40 are applicable for a feeder supplying a building or structure.