I have a 320 amp service with two 200 amp panels. One of them needs to service the main house 300' away. I need a 200 amp disconnect that will handle 300 mcm
Burndy AYPO300 Pin reducer will solve your problem
http://www.ideadigitalcontent.com/files/NEURBRO/4213.pdf
Augie, other than a code violation, what are the safety concerns with just timing the 300 to fit the lug? If timed, there is one less connection that can go bad.
Augie, other than a code violation, what are the safety concerns with just timing the 300 to fit the lug? If timed, there is one less connection that can go bad.
not an issue - but bending space still applies even if you have a reducing device on the end of the conductor - and actually should decrease bending space by the dimension of that reducing device.I posted a while back and was ( did) use # 8's for vd. It was going to be on a 20 amp circuit and going from the 8's to 12's at the breaker or device in the field isn't a problem.
Would reducing the 300's at the breakers (or a box before the breakers ) be an issue ?
I thought I covered both, with conditions for inside the disconnect/breaker enclosure.Ok. I was thinking even box and reduce conductors outside of the enclosures
Enter the enclosures with the smaller conductors ??
One of our members who is sharp on physics can probably elaborate, but Im told "trimming" is particularly bad in that the majority of the current carried by a conductor is carried by the outer strands. I can not testify to the validity of that.
One of our members who is sharp on physics can probably elaborate, but Im told "trimming" is particularly bad in that the majority of the current carried by a conductor is carried by the outer strands. I can not testify to the validity of that.