Looking for suggestions here.
The company has a customer with a 3000 amp 208Y/120 service. The breaker is a GE with a Micro-VersaTrip unit controlling it.
The breaker has tripped a number of times recently and like all good customers they just keep resetting it.:roll:
In looking at the info I can get from the VeraTrip it shows it has tripped 7 times on the short term pick up with the last trip happening with a current of 17.1 kA on phase C.
There are only two feeders from this breaker that I feel could allow a 17.1 kA fault, one is a 700 amp feeder to a stage dimmer rack, the other is an 800 amp feeder to a chiller.
The breaker holds fine for weeks at a time, trips, gets reset and holds for weeks again.
How can I find the cause of this tripping
?