Need help with this and understand it better, we have two 2500 kva transformer,( source A and B), Primary Full-Load Current: 115.751 A
Secondary Full-Load Current: 3007.121 A
Our drawing calls out 12 sets of 500 kcmil, from the transformers feeding our switch gear down stream with A section 3000A and B section 3000A, and a tie in between for backup, let ‘em explain the tie, if B source loses power the tie in between bus A and B closes, meaning both gears are fed from source A, and vise versa, if A looses power B will kick in, my question is should the transformers at full load current be rated for 6000A for this scenario and also what is the reason why the 2500 kva Transformers is calling out for 12 sets of 500 kcmil on the secondary side feeding A or B, but doing the calcs on it, that’s little over 5000 amps.
Secondary Full-Load Current: 3007.121 A
Our drawing calls out 12 sets of 500 kcmil, from the transformers feeding our switch gear down stream with A section 3000A and B section 3000A, and a tie in between for backup, let ‘em explain the tie, if B source loses power the tie in between bus A and B closes, meaning both gears are fed from source A, and vise versa, if A looses power B will kick in, my question is should the transformers at full load current be rated for 6000A for this scenario and also what is the reason why the 2500 kva Transformers is calling out for 12 sets of 500 kcmil on the secondary side feeding A or B, but doing the calcs on it, that’s little over 5000 amps.