I've been posting a lot recently (first time building a new plant) but wanted to thank everyone for their responses and sharing of knowledge. I've said it before and I'll say it again, this site is great!
Our plant has a main 4.16kV 3000A bus with an incoming 5kV breaker set to 3000A. Off of this main bus there are (5) 1200A feeder breakers feeding (5) 1200A 4.16kV buses and a feeder breaker feeing a 6500hp 5kV motor. Ignoring the motor breaker for a second when I add up the (5) 1200A busses which are fed from this main bus I get 6000A which is twice the rating of the main bus. Is this correct? How can 6000A worth of buswork be fed from only a 3000A main bus? I could see if the (5) 1200A breakers that are feeding these (5) busses were set to some lower value but the relay settings shows to set all of these breakers to 1200A.
Is there something that I am missing here? What section of NEC would reference this?
Our plant has a main 4.16kV 3000A bus with an incoming 5kV breaker set to 3000A. Off of this main bus there are (5) 1200A feeder breakers feeding (5) 1200A 4.16kV buses and a feeder breaker feeing a 6500hp 5kV motor. Ignoring the motor breaker for a second when I add up the (5) 1200A busses which are fed from this main bus I get 6000A which is twice the rating of the main bus. Is this correct? How can 6000A worth of buswork be fed from only a 3000A main bus? I could see if the (5) 1200A breakers that are feeding these (5) busses were set to some lower value but the relay settings shows to set all of these breakers to 1200A.