Please see sketch below. I have main service switchboard incoming 8 sets of 750 kcmil Al. There are six main service breakers all 800A.
All horizontal and vertical buses are 3000A. The total calculated demand load comes out to 2950A at the moment but can increase in future.
However, the total six 800A comes out to 800x6= 4800A. How does this protect the 3000A bus? Is their any code regarding this in NEC 2017?
All horizontal and vertical buses are 3000A. The total calculated demand load comes out to 2950A at the moment but can increase in future.
However, the total six 800A comes out to 800x6= 4800A. How does this protect the 3000A bus? Is their any code regarding this in NEC 2017?