Hi Mike,
My 3000W inverter has recommended a 4/0 cable paired with a 300A class T Fuse. I would likely use welding cable for flexibility.
![1683051068760.png 1683051068760.png](https://forums.mikeholt.com/data/attachments/28/28765-19716620475945e68064ca13af7eb559.jpg)
I always double check UL Table 28.1, which states that 4/0 copper cable is only rated for 230A.
![1683050524949.png 1683050524949.png](https://forums.mikeholt.com/data/attachments/28/28763-0a03422089670ef74730104710d9dca3.jpg)
This Chart from Blue Sea Power (doesn't go up to 300A) indicates that 2/0 Battery Cable <20ft is suitable for 200A even though the chart above indicates that it is undersized when referencing table 28.1.
![1683051206068.png 1683051206068.png](https://forums.mikeholt.com/data/attachments/28/28768-e3b1802e81b41ea60b7dcdb6352ef951.jpg)
I've always been taught that its amperage that affects the wire size, so my gut feeling is off on this one.
Thanks for the help and expertise
My 3000W inverter has recommended a 4/0 cable paired with a 300A class T Fuse. I would likely use welding cable for flexibility.
![1683051068760.png 1683051068760.png](https://forums.mikeholt.com/data/attachments/28/28765-19716620475945e68064ca13af7eb559.jpg)
I always double check UL Table 28.1, which states that 4/0 copper cable is only rated for 230A.
![1683050524949.png 1683050524949.png](https://forums.mikeholt.com/data/attachments/28/28763-0a03422089670ef74730104710d9dca3.jpg)
This Chart from Blue Sea Power (doesn't go up to 300A) indicates that 2/0 Battery Cable <20ft is suitable for 200A even though the chart above indicates that it is undersized when referencing table 28.1.
![1683051206068.png 1683051206068.png](https://forums.mikeholt.com/data/attachments/28/28768-e3b1802e81b41ea60b7dcdb6352ef951.jpg)
I've always been taught that its amperage that affects the wire size, so my gut feeling is off on this one.
Thanks for the help and expertise