Hi all, Just wanted to get confirmation that what I am planning to do is compliant, I?ve never done a 300 Amp service this way before. I plan to use a 325/400 amp meter pan which is to be mounted on a post 90 feet from the house. A 2.5 inch pvc conduit carries the service conductors into the garage of a single family dwelling, where I plan to install a 200A service panel and a 100A service panel. I plan to install two sets of service conductors in the 2.5 inch pvc, one sized for the 200A and one for the 100A (meter pan has dual load side lugs) I guess the two things I am not quite sure of are:
1. Can two sets of different sized service conductors be installed in the same pipe? They are not paralled, they just each feed their respective panels. 230.7 states that "conductors other than service conductors shall not be installed in the same raceway" so presumable there is no problem unless another article applies.
2. How is diversity interpreted when more than three current carrying conductors are installed in the same raceway? Do I have to derate 80% per table 310.15(B)(2)(a)? Obviously the chance of each panel being even close to fully loaded at he same time is minimal. I also just noticed that table 310.15(B)(2)(a) states the adjustments are for tables 310.16-310.19, but what if I am using table 310.15(B)(6) to size my conductors?
Thanks everyone, Ethan.
1. Can two sets of different sized service conductors be installed in the same pipe? They are not paralled, they just each feed their respective panels. 230.7 states that "conductors other than service conductors shall not be installed in the same raceway" so presumable there is no problem unless another article applies.
2. How is diversity interpreted when more than three current carrying conductors are installed in the same raceway? Do I have to derate 80% per table 310.15(B)(2)(a)? Obviously the chance of each panel being even close to fully loaded at he same time is minimal. I also just noticed that table 310.15(B)(2)(a) states the adjustments are for tables 310.16-310.19, but what if I am using table 310.15(B)(6) to size my conductors?