I got a call from one of our guys today. Customer has a 300A 1? genny. A 2" schedule 40 was slabbed a while back for this. House has a 600A service.
This is what I got:
300A = 350kcmil
3 350 thhn = 1.5726 in.?
1 #4 thhn= .0824 in?
1.5726+.0824=1.655 in?
2" sched 40 =1.316
That doesn't work
Parallel:
2/0 = 195?.8=156A (as per 310.15(B)(2)(a)
6 2/0 thhn = 1.3338 in?
Already over without the #4 EGC.
As a note this is a manual transfer switch operation. I would have to guess that the actual load is over 300A.
Anybody have a miracle up their sleeve?:grin:
This is what I got:
300A = 350kcmil
3 350 thhn = 1.5726 in.?
1 #4 thhn= .0824 in?
1.5726+.0824=1.655 in?
2" sched 40 =1.316
That doesn't work
Parallel:
2/0 = 195?.8=156A (as per 310.15(B)(2)(a)
6 2/0 thhn = 1.3338 in?
Already over without the #4 EGC.
As a note this is a manual transfer switch operation. I would have to guess that the actual load is over 300A.
Anybody have a miracle up their sleeve?:grin: