kingelectric
Member
On the job today there was a 300kva 480v - 120/208v transformer ,they had 2- 2'' conduits feeding the 480v primary side with 3- 3/0 copper wires in each conduit with a ground in each. I would think you would need 4/0 copper to feed this . The 480v has a 360amp rating. any thoughts on this and will the 4/0 still fit in the 2'' conduit? the distance is about 325'