Isosynchronous
New member
We are being asked to install a new 480 volt 3 phase 3 wire 600 amp copper feeder to a distribution board at a machine shop to replace an existing aluminum feeder that was damaged by a forklift. Our plan was to run 2 parallel runs of 300MCM THHN copper wire in (2) 3" EMT Conduits, approximately 150 feet in length, with one # 1 CU ground wire in each conduit. The existing 600 amp feeder circuit breaker is 80% rated and the terminations are rated for 75 Deg C. The ambient temperature in the shop is less than 40 Deg C. The maximum calculated full load current draw of all of the loads present on the existing the distribution board is 430 Amperes. Is 2 sets of 300MCM Copper wire feeders an acceptable installation?