I followed a thread which unfortunately was closed before I could comment.
The discussion was on 300V wire in a 480V contactor.
A senior member wrote;
"Section 300.3(C)(1) makes it clear that the maximum circuit voltage in the raceway, not the maximum insulation voltage rating of the conductors in the raceway, is what determines the minimum voltage rating required for the insulation of conductors for systems of 600 volts or less.
The conductors of a 3-phase, 4-wire, 208Y/120-volt ac circuit; a 3-phase, 4-wire, 480Y/277-volt ac circuit; and a 3-wire, 120/240-volt dc circuit may occupy the same equipment wiring enclosure, cable, or raceway if all the conductors are insulated for the maximum circuit voltage of any conductor. In that case, the maximum circuit voltage would be 480 volts, and 600-volt insulation would be suitable for all the conductors.
If a 2-wire, 120-volt circuit is included in the same raceway with a 3-wire, 120/240-volt circuit having 600-volt conductors, the 2-wire, 120-volt circuit conductors could use 300-volt insulation because the maximum circuit voltage is only 240 volts.
Raceway. An enclosed channel of metal or nonmetallic materials designed expressly for holding wires, cables, or busbars, with additional functions as permitted in this Code. Raceways include, but are not limited to, rigid metal conduit, rigid nonmetallic conduit, intermediate metal conduit, liquidtight flexible conduit, flexible metallic tubing, flexible metal conduit, electrical nonmetallic tubing, electrical metallic tubing, underfloor raceways, cellular concrete floor raceways, cellular metal floor raceways, surface raceways, wireways, and busways.
Though it is not precisely defined I've considered J boxes, pull boxes, gutters, & panels part of the raceway system."
Everyone seems to miss the important wording in NEC 300.3(C)(1):
All conductors shall have an insulation rating equal to at least the maximum circuit voltage APPLIED TO ANY CONDUCTOR within the enclosure, cable, or raceway.
Yes there is 480V present within the enclosure, however each conductor is supplying 277V.
At no time would you have more then 277V on any one conductor unless there is a problem where the neutral and/or ground reference point have been compromised in which case you will have bigger problems to contend with anyway.
So the way I interpret this code section, it IS permissible to have 300V rated wire in a 480V system, enclosure, multi-conductor cable, or raceway.
Discussion please???
The discussion was on 300V wire in a 480V contactor.
A senior member wrote;
"Section 300.3(C)(1) makes it clear that the maximum circuit voltage in the raceway, not the maximum insulation voltage rating of the conductors in the raceway, is what determines the minimum voltage rating required for the insulation of conductors for systems of 600 volts or less.
The conductors of a 3-phase, 4-wire, 208Y/120-volt ac circuit; a 3-phase, 4-wire, 480Y/277-volt ac circuit; and a 3-wire, 120/240-volt dc circuit may occupy the same equipment wiring enclosure, cable, or raceway if all the conductors are insulated for the maximum circuit voltage of any conductor. In that case, the maximum circuit voltage would be 480 volts, and 600-volt insulation would be suitable for all the conductors.
If a 2-wire, 120-volt circuit is included in the same raceway with a 3-wire, 120/240-volt circuit having 600-volt conductors, the 2-wire, 120-volt circuit conductors could use 300-volt insulation because the maximum circuit voltage is only 240 volts.
Raceway. An enclosed channel of metal or nonmetallic materials designed expressly for holding wires, cables, or busbars, with additional functions as permitted in this Code. Raceways include, but are not limited to, rigid metal conduit, rigid nonmetallic conduit, intermediate metal conduit, liquidtight flexible conduit, flexible metallic tubing, flexible metal conduit, electrical nonmetallic tubing, electrical metallic tubing, underfloor raceways, cellular concrete floor raceways, cellular metal floor raceways, surface raceways, wireways, and busways.
Though it is not precisely defined I've considered J boxes, pull boxes, gutters, & panels part of the raceway system."
Everyone seems to miss the important wording in NEC 300.3(C)(1):
All conductors shall have an insulation rating equal to at least the maximum circuit voltage APPLIED TO ANY CONDUCTOR within the enclosure, cable, or raceway.
Yes there is 480V present within the enclosure, however each conductor is supplying 277V.
At no time would you have more then 277V on any one conductor unless there is a problem where the neutral and/or ground reference point have been compromised in which case you will have bigger problems to contend with anyway.
So the way I interpret this code section, it IS permissible to have 300V rated wire in a 480V system, enclosure, multi-conductor cable, or raceway.
Discussion please???