Re: 300V Motor Full Load Current.
I suspect the motor(s) you are describing are either not for US domestic use or are for "specialty" applications.
Especially for low voltage applications, Art 430 "leans" very heavily toward NEMA "standard" motors. (Certain nameplate requirements in 430.7 definitely reflect NEMA and not foreign standards) While NEMA MG-1 recognizes both 50 & 60 Hz, it does not recognize non-standard voltages.
Table 430.150 is based on the highest FLA for any standard motor size that any NEMA manufacture makes. This permits general interchangeability of NEMA motors of the same HP and frame size without requiring the entire installation to be ?re-engineered.? It also provides a relatively conservative basis for initial load calculations.
All that being said, if this is an engineered system for ?specialty applications?, interpolating the values in Table 430.150 should meet your needs.