Folks, could not find any previous posts regarding this-I hope it's not a repetitive question.
Existing pool we renovated (35yrs old). (2) existing 300W/ 12V lights powered by (2) separate Intermatic 300W transformers. We installed new deck boxes, conduit and re-wired for both lights. Bonding is sound.
One light was not working so I started from the source. 110V power to transformers. 12V at transformer loads.
The deck boxes are approx. 50' and 75' from the transformers respectively. The furthest light is the one not working.
During testing I checked the power to the closest deck box without hooking up to the light that is working. I got 12V. The furthest deck box, to the light not working, I got the same. Ok, so I determined this light fixture or bulb is shot.
When I connected the closer light that is working, and tested, my voltage dropped almost in half. The Intermatic transformers give you (3) choices of output power 12,13 and 14V. I rewired for 13V and still had about 6.2-3V.
This light is working but is it on it's way out? What would cause the big draw? These are standard bulbs not LED's. The lights are not originals.
Existing pool we renovated (35yrs old). (2) existing 300W/ 12V lights powered by (2) separate Intermatic 300W transformers. We installed new deck boxes, conduit and re-wired for both lights. Bonding is sound.
One light was not working so I started from the source. 110V power to transformers. 12V at transformer loads.
The deck boxes are approx. 50' and 75' from the transformers respectively. The furthest light is the one not working.
During testing I checked the power to the closest deck box without hooking up to the light that is working. I got 12V. The furthest deck box, to the light not working, I got the same. Ok, so I determined this light fixture or bulb is shot.
When I connected the closer light that is working, and tested, my voltage dropped almost in half. The Intermatic transformers give you (3) choices of output power 12,13 and 14V. I rewired for 13V and still had about 6.2-3V.
This light is working but is it on it's way out? What would cause the big draw? These are standard bulbs not LED's. The lights are not originals.