30A 240V FUSED SAFETY SWITCH
mstrlucky74
NJ
If the above switch is a 2 pole switch doesn't it have to be feed from a 2P breaker? I ask because it is showing it being fed from a 1P 20A breaker. Although, I do see in the description below it says there is an option for 3HP @ 240V 1phase. Can these switched be fed single phase? This is were I need a little wiring/theory insight.
SQUARE D
Mfr Brand Name:SQUARE D/TELEMECANIQUE
Catalog No.:H221N
UPC:785901-47768
GTIN:00785901477686
TRA-SER PIK:598183
Product Name: SAFETY SWITCH
Description:SWITCH FUSIBLE HD 240V 30
Commodity:31310 - Fusible Heavy Duty Safety Switches
Long
Description:
HEAVY DUTY SAFETY; 240 V AC VOLTAGE; 250 V DC VOLTAGE; 30 AMPERE; POWER RATING 1 1/2 HP AT 240 VAC 1 PHASE, 3 HP AT 240 VAC 3 PHASE (STANDARD); 3 HP AT 240 VAC 1 PHASE, 7 1/2 HP AT 240 VAC 3 PHASE (MAXIMUM); 5 HP AT 250 VDC; 2 POLE; 3 WIRE; CLASS R FUSE; FUSIBLE FUSE; SOLID NEUTRAL; NEMA 1; SIZE 7.55 INCH W X 4.88 INCH D X 14.6 INCH H; APPROVAL UL, CSA; SQUARE D[R] BRAND
Country Of Origin: United States
SQUARE D
Catalog No.:H221N
UPC:785901-47768
GTIN:00785901477686
TRA-SER PIK:598183
Long
Description:
Double pole and 240V single phase are the same thing. You are confusing 3? with single phase. Single phase can be 1-pole or 2-pole.
The switch is a 2-pole, but can be used with a single pole feed.
Got it, was not sure if you could utilize only 1P. Thanks.