30A CB for 120V lighting circuit

Status
Not open for further replies.

anbm

Senior Member
Existing building has (5) 400W MH @120V exterior lights, somehow they wired to 20A/1P CB, in 208Y/120V panel.

We want to replace above 20A CB in existing panel by new 30A CB, change wires to 30A and re-feed existing lights.

Haven't used 30A CB to feed 120V lights before so not sure if this allows? Thank you.
 

kwired

Electron manager
Location
NE Nebraska
Existing building has (5) 400W MH @120V exterior lights, somehow they wired to 20A/1P CB, in 208Y/120V panel.

We want to replace above 20A CB in existing panel by new 30A CB, change wires to 30A and re-feed existing lights.

Haven't used 30A CB to feed 120V lights before so not sure if this allows? Thank you.

It can be done. I would be more likely to change the taps to 208 volts (if that is possible) and supply with a 208 volt circuit in most instances.
 

mjmike

Senior Member
"Thank you. BTW, I found 210.23 (B) allows it."


I disagree for 2 reasons. First reason, a fixed light fixture I doubt would be considered a lampholder. I believe it would be classified as a luminaire per the definition of luminaire. Next, if that is not good enough. Refer to 210.21A commentary and what a heavy duty lampholder is considered.
 

K8MHZ

Senior Member
Location
Michigan. It's a beautiful peninsula, I've looked
Occupation
Electrician
"Thank you. BTW, I found 210.23 (B) allows it."


I disagree for 2 reasons. First reason, a fixed light fixture I doubt would be considered a lampholder. I believe it would be classified as a luminaire per the definition of luminaire. Next, if that is not good enough. Refer to 210.21A commentary and what a heavy duty lampholder is considered.

I had to look it up, but I did find that 'admedium' meant an E29 Edison Screw base.

So he has to make sure the lampholders in the 450 watt fixtures are rated at 750* watts or more, then he's good, correct? *Or 660 for an E29.
 

K8MHZ

Senior Member
Location
Michigan. It's a beautiful peninsula, I've looked
Occupation
Electrician
Here is a technical question.....

Are the lampholders connected to the branch circuit? I agree that the luminaire is, but the lampholder in a MH fixture is isolated from the branch circuit through the ballast, is it not?

Edit...

I read read, and I guess it doesn't matter.

Nevermind.....

:)
 
Last edited:

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
So he has to make sure the lampholders in the 450 watt fixtures are rated at 750* watts or more, then he's good, correct? *Or 660 for an E29.

I'd say this is correct. And since the 400W MH lampholder is most likely a mogul base, and I've never see a mogul base with a rating less than 750W, he's probably OK. Of course, there's always a chance things aren't as expected.
 