Re: 30A O.C.P. FOR LIGHTING
sam34, For this application I would run the 30 40 or 50 amp feeder from pole to pole and specify inline fuseholders (something like Bussman Type KK fuses) and tap from the feeder at the pole handhole. 1000W heads in a parking area is probably 2, 3, or 4 heads per pole and there should be ample space to have the fuseholders installed at the handhole access. Each luminaire would tap from the main feeder (which could be #8 #6 or #4 depending upon load and VD factors) and the wiring that runs from the tap to the luminaire could be #12.
For additional capacity of the circuit the feeder that runs to each pole could be a 3 phase feeder, and the 480 or 208 volt luminaires could tap from the phase legs A-B, A-C, B-C etc to ensure balanced loading. This will enable additional capacity with each circuit at the cost of pulling another phase leg.
Lets assume 480 volt, 30a 3 phase circuit.
30 x .8 = max continuos load of 24 amps.
24 x 830 = 19920 max va
19920 / 1250W (1000W head w/ ballast load) = 15.936
Therefore 15 heads (balanced on the 3 phases of course) on a 30a-3ph circuit would be the maximum.
Consider that against a 480 volt 20a-1ph circuit, which could carry a maximum of 6 luminaires.