I observed an existing installation with 30A 208V receptacles with 3/12 MC cable spliced to #10 THHN wire that runs back to the panel that lands on a 20A/2P breaker. A centrifuge is plugged into the receptacle and the nameplate data lists its ampacity at 20A. While this doesn't seem like a good design, is it Code compliant? Is there anywhere in the Code that says you can't have a 20A circuit connected to a 30A receptacle? Also, I believe the 20A circuit breaker would need to be 100% rated. Opinions?