30A Service

Status
Not open for further replies.
I'm looking at 230-79 (b) where NEC allows (I hope still, I'm looking at NEC1999) 30A Service. It then goes on to say..."of not more than two 2-Wire branch circuits,..." What is meant by this? Assuming the service is 240/120 Single Phase, does this allow me up to two 2-pole circuits? I have searched under definitions, and can't find a definition for 2-Wire branch circuit. Any help will be appreciated.
 
A two wire branch circuit is ONE 120 volt circuit or ONE 240 volt circuit. A 120 volt multiwire branch circuit is a 3-wire circuit, and a 120/240 circuit (dryer, range) is a 4-wire circuit.

30 amp services normally serve things like remote signs, remote pumps, remote transmitters, billboards, school crossing signals, and small apartments in a multiple occupancy building. A single family dwelling, in a building by itself, still needs at least a 100 amp service.

Naturally, POCO rules prevail. For instance, all the one's I deal with want the line side of the meter to be served with at least 100 amp sized conductors. This, in my opinion, has more to do with the sizes of taps and crimps they carry on the line trucks more than anything. You won't be able to terminate #10 copper to the load side of a meter can, so you'll be putting some #3 in the load side meter lugs (or whatever scrap you have handy) and tapping that onto your #10.

Expect strange looks from your inspector.
 
Last edited:
There are two components being addressed in the section. The service disconnect rating, and the branch circuit rating(s). IMO, in the section in question, they're saying a single 30A handle shall disconnect a panelboard supplying 2 two-wire branch circuits.
 