I have three 2pole 30amp GFCI breakers in my shop. The panel and breakers are all SquareD Homeline series. I just got a new 5HP 20" planer that I plugged into one of the circuits. It immediately tripped the breaker when I turned it on. It seems to trip the breaker roughly 4 out of 5 start attempts. My 3hp tablesaw will run when connected to the same receptacle with no problems, which is why this is a new problem to me. The circuits are all new (less than 6 months old, and the shop I am building is still under constructiuon inside. To troubleshoot the problem I have done the following:
1) I opened up the receptacle and verified there were no loose wires or short circuits.
2) I moved the 5hp planer to both of the other 30amp circuits, and it runs just fine on those circuits. No trips at all.
3) I swapped two of the 30amp breakers and the tripping issue follows the breaker, ruling out a circuit issue.
My question is this. Is it possible that I just have a weak breaker that is tripping too low and is just defective?
1) I opened up the receptacle and verified there were no loose wires or short circuits.
2) I moved the 5hp planer to both of the other 30amp circuits, and it runs just fine on those circuits. No trips at all.
3) I swapped two of the 30amp breakers and the tripping issue follows the breaker, ruling out a circuit issue.
My question is this. Is it possible that I just have a weak breaker that is tripping too low and is just defective?