I agree with Don also, but 240.86 refers to circuit breakers not fuses. Systems can be series rated by engineering supervision or manufacturer tested systems. All downstream devices can be protected using fuse let thru ratings with proper coordination. Circuit breaker series ratings can only be taken as single tier (as tested) and listed by the manufacturer, so I don't think you will find a circuit breaker to motor starter series rating (though I don't know this for a fact, maybe someone knows better). Some areas of the country make you take the available fault current of the utility transfomer at the main disconnect without any reduction (which I don't understand, but that's the way it is). If you are series rating using fuses (or circuit breakers) to protect downstream devices, you still need to provide proper labeling at the interrupting device. See 110.9, 110.10, 110.22(B) and 110.22(C). Also remember that the future is a long time, I have seen many instances when the utility will change transformers for many reasons and the existing systems are no longer protected for the new available fault currents.