I have a 30kva 480v primary 208v secondary transformer I?m wiring. My question is what size ocd should I use for the primary side? I've calculated a 45 amp breaker is needed but can I round up or should I always round down?
30,000va\ (480x1.732) =36.08A
36.08A x 1.25=45.1
I?m using a 50amp breaker on the primary side.
I did browse other posts but found nothing with this particular example.
Any help will be appreciated.