On a 30kva Three phase 480 delta ,120/ 208 Y. why would you calculate 83 amps at 208 if most of the circuits being used will be at 120v?
That is incorrect. VL = 208, VP= 120. Like Augie said, you could look it at as (3) 10kVA 120V transformers --> 10kVA / 120V = 83A, or if you look at it as 3-phase, 30kVA divided by (208V * 1.73) that will give you the 83A.Thanks gentlemen, I was over thinking You have to calculate 120 x 1.73 to get 208. So I will get 83 amps per phase.
My math is wrong But Per phase is still 83 amps correct? so in a three phase panel My main will be 100 amp with capability of pulling 83 amps per phase which will give me a panel compacity of 249 if equally distributed between phases.That is incorrect. VL = 208, VP= 120. Like Augie said, you could look it at as (3) 10kVA 120V transformers --> 10kVA / 120V = 83A, or if you look at it as 3-phase, 30kVA divided by (208V * 1.73) that will give you the 83A.
They are not taking into account phase vectors.249 x 120 = 30,000
Understood but I thought I might help answer the initial question in a simplified form.They are not taking into account phase vectors.
30 amps per phase?They are not taking into account phase vectors.
Rounding up to 30, sure. In simple 100% balance, take 83A from the 3-phase calculations and divide it by 3. that gives you 28A per phase.30 amps per phase?