On a 30kva Three phase 480 delta ,120/ 208 Y. why would you calculate 83 amps at 208 if most of the circuits being used will be at 120v?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
It may help if you look at a 208Y/120 30kva 3 phase transformer as (3) 10kva 120v transformers. Same answer 83 amps.
 

Rock86

Senior Member
Location
new york
Occupation
Electrical Engineer / Electrician
Thanks gentlemen, I was over thinking You have to calculate 120 x 1.73 to get 208. So I will get 83 amps per phase.
That is incorrect. VL = 208, VP= 120. Like Augie said, you could look it at as (3) 10kVA 120V transformers --> 10kVA / 120V = 83A, or if you look at it as 3-phase, 30kVA divided by (208V * 1.73) that will give you the 83A.
 

pushbutton

Member
Location
Faythe629
Occupation
electrical
That is incorrect. VL = 208, VP= 120. Like Augie said, you could look it at as (3) 10kVA 120V transformers --> 10kVA / 120V = 83A, or if you look at it as 3-phase, 30kVA divided by (208V * 1.73) that will give you the 83A.
My math is wrong But Per phase is still 83 amps correct? so in a three phase panel My main will be 100 amp with capability of pulling 83 amps per phase which will give me a panel compacity of 249 if equally distributed between phases.
 

Rock86

Senior Member
Location
new york
Occupation
Electrical Engineer / Electrician
It doesn't work like that exactly. Plain and simply... if you have a 3-phase system with a 30kVA transformer supplying a 120/208 3-phase system, your capacity would be 83A.
 