I ike5547 Senior Member Location Chico, CA Occupation Electrician Aug 24, 2010 #2 My first guess is about 25 gazillion.
I ike5547 Senior Member Location Chico, CA Occupation Electrician Aug 24, 2010 #3 or 25 amps according to 411.2
I ike5547 Senior Member Location Chico, CA Occupation Electrician Aug 24, 2010 #4 mj324 said: whats max amps allowed on 30v or less lt system Click to expand... What kind of layout are you considering? The 25 amp limitation seems to be per secondary circuit. You could add more.
mj324 said: whats max amps allowed on 30v or less lt system Click to expand... What kind of layout are you considering? The 25 amp limitation seems to be per secondary circuit. You could add more.
M mj324 Member Aug 24, 2010 #5 30 v lt 30 v lt this was a ? on a test i seeat 411 where it says 25 but when you look at 411.6 it says 20 amps
30 v lt 30 v lt this was a ? on a test i seeat 411 where it says 25 but when you look at 411.6 it says 20 amps
I ike5547 Senior Member Location Chico, CA Occupation Electrician Aug 24, 2010 #6 That's the primary (line side) of the transformer.
I ike5547 Senior Member Location Chico, CA Occupation Electrician Aug 24, 2010 #7 Looking again at 411.6 it sure is worded vaguely. I'm sure the intent is the primary side current but they sure could have done a better job writing it.
Looking again at 411.6 it sure is worded vaguely. I'm sure the intent is the primary side current but they sure could have done a better job writing it.