C captainwireman Senior Member Location USA, mostly. Apr 6, 2014 #1 Am I correct saying the A phase set of paralleled conductors can be longer than the C phase set if all other conditions are met?
Am I correct saying the A phase set of paralleled conductors can be longer than the C phase set if all other conditions are met?
G GoldDigger Moderator Staff member Location Placerville, CA, USA Occupation Retired PV System Designer Apr 6, 2014 #2 Yes. The matching requirement applies only to the conductors of each phase seperately. Tapatalk!
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Apr 6, 2014 #3 GoldDigger said: Yes. The matching requirement applies only to the conductors of each phase separately. Tapatalk! Click to expand... I agree... In fact they may be different characteristics also. Thus "A" phase may be copper and "B" phase may be aluminum but you wont see that often