Electrical PE
Member
- Location
- MA, USA
I have a large battery bank with a main disconnect at its output rated for 1400A. At the output of the disconnect, there are (3) 500A fuses paralleled between (2) buses, one on each side of the fuses (done by the manufacturer).
On the other side I have a recombiner of an inverter that has individual fused inputs. Max fuse size that can be connected to it is 400A.
The intended connection is to run 5 sets on conductors in parallel from the bus at the output of the battery unit and terminating them on 5 individual 350A fused inputs in the recombiner. These 5 fuses are connected to the main bus of the recombiner.
Conductors are same length, same material, same size, same insulation, and terminated in the same manner.
Is this connection violating any of the requirements in this article? Including the requirement for parallel conductors to be "electrically joined at both ends" mentioned in 310.10(H)(1)? or it is considered code-compliant?
Thank you
On the other side I have a recombiner of an inverter that has individual fused inputs. Max fuse size that can be connected to it is 400A.
The intended connection is to run 5 sets on conductors in parallel from the bus at the output of the battery unit and terminating them on 5 individual 350A fused inputs in the recombiner. These 5 fuses are connected to the main bus of the recombiner.
Conductors are same length, same material, same size, same insulation, and terminated in the same manner.
Is this connection violating any of the requirements in this article? Including the requirement for parallel conductors to be "electrically joined at both ends" mentioned in 310.10(H)(1)? or it is considered code-compliant?
Thank you