Any help explain this please.
310.12 says "the service conductors supplying the entire load associated with a one-family dwelling, shall be permitted to have an ampacity not less than 83 percent of the service rating"
230.42 says "Service-entrance conductors must have an ampacity not less than the maximum load to be served"
So my service is 400A and my load is 355.
Do just apply the reduction to the whole service 400A x .83 and size the wire for 332A with parallel 4/0 AL, or do i have to use the whole load 355A and use parallel 250Kcm AL?
310.12 says "the service conductors supplying the entire load associated with a one-family dwelling, shall be permitted to have an ampacity not less than 83 percent of the service rating"
230.42 says "Service-entrance conductors must have an ampacity not less than the maximum load to be served"
So my service is 400A and my load is 355.
Do just apply the reduction to the whole service 400A x .83 and size the wire for 332A with parallel 4/0 AL, or do i have to use the whole load 355A and use parallel 250Kcm AL?