wwhitney
Senior Member
- Location
- Berkeley, CA
- Occupation
- Retired
Let's say we have a residential service going to a Class 320 meter/main with (2) 200A OCPD. 230.90(A) Exception 3 says that the SEC ampacity only needs to be at least the calculated load, not necessarily a full 400A. And 310.12(A) says the SEC ampacity only has to be 83% of the "service rating".
Further, let's say the load calculation comes out to 360A non-continuous, no ampacity adjustment or correction is required, and the meter socket has 75C line side terminals. May we choose to install 350 kcmil Cu SECs? Possible answers below.
Cheers, Wayne
Answer (1): 350 kcmil Cu SECs have a 75C ampacity of 310A. 310/0.83 = 373A, so we have a 373A "service rating". No problem with 360A calculated load.
Answer (2): "Service rating" has to be a standard OCPD size. So we can just look at Table 310.12, and see that 350 kcmil Cu SECs correspond to a 350A service rating. Too small for a 360A calculated load.
Answer (3): Other?
Further, let's say the load calculation comes out to 360A non-continuous, no ampacity adjustment or correction is required, and the meter socket has 75C line side terminals. May we choose to install 350 kcmil Cu SECs? Possible answers below.
Cheers, Wayne
Answer (1): 350 kcmil Cu SECs have a 75C ampacity of 310A. 310/0.83 = 373A, so we have a 373A "service rating". No problem with 360A calculated load.
Answer (2): "Service rating" has to be a standard OCPD size. So we can just look at Table 310.12, and see that 350 kcmil Cu SECs correspond to a 350A service rating. Too small for a 360A calculated load.
Answer (3): Other?