Jimmy7
Senior Member
- Location
- Boston, MA
- Occupation
- Electrician
I had a relative ask me to wire their new addition on their house. I told them I was too busy because I didn’t want to get involved ( You get it). In any case, they hired an electrician to wire the addition, I just recently got to see the completed rough while over visiting their home. I noticed that the electrician ran a 100 amp subpanel below the addition with a 4-3 romex. Obviously, this subpanel doesn’t carry the entire load of the house, so the electrician shouldn’t have used 310.12 to choose #4, correct? He should have used #3 copper (Example pipe and wire for #3 copper) from 310.16, correct? I kept my mouth shut about it. I was thinking how would I explain (Which I won’t) that you can use a #4 for a feeder if it handles the “Entire Load”, but you have to use a larger conductor when it handles a partial load?