Devin Hanes
Member
- Location
- United States
I would appreciate any thoughts on the following Public Input I am working on, Thank you.
310.12 Single-Phase Dwelling Services and Feeders
Change
I am asking to remove the allowance for 120/208 Three-phase Services. And add some clarifying language to the table title consistent with the other tables. (I will have the proposed revised language in my next post)
Substantiation
The allowance made in the 2017 edition for 120/208 3 wire services allows and promotes a fire hazard. The Edison three-wire single phase 120/240 under normal operation will only ever be exposed to the equivalent temperature rise of two fully loaded conductors (two heaters), while a neutraled 3-wire service from a three-phase system will allow all three conductors(heaters) to be fully loaded, exposing the conductor group to the temperature rise of three conductors (50% more than the Edison 3-wire). Our 310.16 table is based on 3 conductors fully loaded in a conductor group, the Edison 3 wire effectively only has 2 loaded, and also benefits from the heat sink properties of the effectively third conductor not carrying current, further lowering the operating temperature of the conductor group.
The reasoning behind the original allowance for the entire section appears to have been lost by some of the code making panel an industry over the years, which is probably why 120/208 was mistakenly added to the original allowance. It appears the panel believes this allowance is due to the diversity of the loads served, when it is actually because of load diversity of the conductors(2 heaters instead of 3), I will provide clear historical proof.
Please see historical highlights of this allowance below and attached (under additional proposed changes), to illustrate the reasoning behind the allowance of the section (expanded versions attached). (I will post attachments in future posts)
Before 1956 there was no special allowance for the service conductors.
1956
NFPA Proceedings of the sixth annual meeting June 4-8, 1956
Page 52 and 53
Report of Electrical Correlating committee
“Also in connection with this table, the utility people pointed out that aluminum wire for services was being modified from the 84 per cent value previously given in the Code, that is 84 per cent of the copper carrying capacity, and while they were in agreement with that because the data was the result of a study by the sub-committee, they did want to point out that in a 3-wire single phase, with only one of the wires loaded, it would not be necessary to go to the higher values.
It was proposed that a note be made for 2 to 4/0, the allowable capacity, it would be one, the 84 percent value, and these values were ironed out by the Correlating Committee to values normally used by the Code so that for #2, 100 amperes; #1, 110 amperes; for #0, 120. That, too, was adopted by the Correlating Committee. There were minor editorial changes but those are the changes in substance."
Historical panel comments on not using 3 phase are attached under (additional proposed changes)
1956 NEC
Table 1A, Page
(attached) you will note the allowance was for all single phase 3-wire edison services not just residential or even 120/240 (see the table notes for the allowance)
1956 AIEE (Became IEEE later) Paper "The Heating and Mechanical Effects of Installing Insulated Conductors in Steel Raceways" By Brandon, Kline, Geiges and Paradise. https://ieeexplore.ieee.org/document/4499473
"Purpose
The purpose of the investigation was to
compile information, observations, and
test data which could be used for analyzing
the following:
1. The applicable, current-carrying capacity
reduction factors for more than nine
conductors.
2. The effect of load diversity in reference
to the current-carrying capacity reduction
factors and conductor-operating temperatures."
This entire article is available online from IEEE, I am sending a copy of the test findings chart that illustrates the use of the term "load diversity" as not meaning the actual load being served, but the number of conductors conducting.
The chart is titled Table VIII. Diversity Tests, column titles are Wire Type, Wire Size AWG, No. of Wires, No. Conducting, Operating Temperature C, Amperes, and Volts. The first row of data is #6 AWG, 12 wires, 4 conducting, operating at 60C, 59.5Amperes and 3.5 Volts. This testing was used for our De-rating table.
The Submitter for the 17' change even shows these conductor current differences(heaters) in his attachment (attached to this input). You are allowing three heaters in an assembly instead of two, all heaters being of the same BTU output, while also eliminating the heat sink properties of the equivalence of a 0 current third conductor. The heating difference is due to three phase being 120 degrees out of phase while the edison 3 wire is 180 degrees out of phase resulting in neutral only carrying current if there is imbalance, the three phase neutral will carry 200 amps when both of the 208 legs are carrying 200 amps, it doesn't "cancel". The I^2R power loss equation shows you have three heaters compared to two equivalent, I^2R, (Current Squared X the Resistance of the Wire).
Also, If the conductors are large enough for the residential load, then the normal over-current protection device is also large enough, there is only bad reasoning to allow a larger OCPD on THE MOST SENSITIVE conductor group in the MOST VULNERABLE type of building construction. What I mean by that is service conductors only have OCPD, not upstream short circuit protection like other conductors, so if these are overloaded even just slightly just occasionally after a long period of time the result will be a fire, there's no safety left, it was eliminated with this allowance, you have no appropriate OCPD. And dwelling units are wood framed with a continual decline in fire resistance due to the materials used, houses burn much easier, faster and hotter when built out of the common materials used today compared to decades past.
If the conductors are large enough for the load then the normal OCPD is as well. I am sending a copy of common OCPD trip curves, the Square D 175Amp would take a minimum of 20.83 minutes to trip at 175 amps all the way up to 2.78 hours. At 218 amps its about 5.83 minutes to 2.78 hours. Why would a 175 amp residential service ever need to operate at 175 amps for longer than 20 minutes which is the minimum time it will take ocpd to open.
There’s well more than enough wiggle room in OCPD curves to not need this allowance, just use a smaller breaker, if the wire's big enough then the normal OCPD is as well. Also, the CEC allowance does not prove it to be safe, table 310.16 values are based on legitimate testing while the CEC allowance is not. The allowance does not mean the service will definitely result in fire it just unnecessarily removes protection, so the fact that we don't have reports of these services burning up everywhere is not a legitimate argument for fast-tracking this allowance past legitimate testing.
I will add the referenced attachments in my next posts, Thanks.
310.12 Single-Phase Dwelling Services and Feeders
Change
I am asking to remove the allowance for 120/208 Three-phase Services. And add some clarifying language to the table title consistent with the other tables. (I will have the proposed revised language in my next post)
Substantiation
The allowance made in the 2017 edition for 120/208 3 wire services allows and promotes a fire hazard. The Edison three-wire single phase 120/240 under normal operation will only ever be exposed to the equivalent temperature rise of two fully loaded conductors (two heaters), while a neutraled 3-wire service from a three-phase system will allow all three conductors(heaters) to be fully loaded, exposing the conductor group to the temperature rise of three conductors (50% more than the Edison 3-wire). Our 310.16 table is based on 3 conductors fully loaded in a conductor group, the Edison 3 wire effectively only has 2 loaded, and also benefits from the heat sink properties of the effectively third conductor not carrying current, further lowering the operating temperature of the conductor group.
The reasoning behind the original allowance for the entire section appears to have been lost by some of the code making panel an industry over the years, which is probably why 120/208 was mistakenly added to the original allowance. It appears the panel believes this allowance is due to the diversity of the loads served, when it is actually because of load diversity of the conductors(2 heaters instead of 3), I will provide clear historical proof.
Please see historical highlights of this allowance below and attached (under additional proposed changes), to illustrate the reasoning behind the allowance of the section (expanded versions attached). (I will post attachments in future posts)
Before 1956 there was no special allowance for the service conductors.
1956
NFPA Proceedings of the sixth annual meeting June 4-8, 1956
Page 52 and 53
Report of Electrical Correlating committee
“Also in connection with this table, the utility people pointed out that aluminum wire for services was being modified from the 84 per cent value previously given in the Code, that is 84 per cent of the copper carrying capacity, and while they were in agreement with that because the data was the result of a study by the sub-committee, they did want to point out that in a 3-wire single phase, with only one of the wires loaded, it would not be necessary to go to the higher values.
It was proposed that a note be made for 2 to 4/0, the allowable capacity, it would be one, the 84 percent value, and these values were ironed out by the Correlating Committee to values normally used by the Code so that for #2, 100 amperes; #1, 110 amperes; for #0, 120. That, too, was adopted by the Correlating Committee. There were minor editorial changes but those are the changes in substance."
Historical panel comments on not using 3 phase are attached under (additional proposed changes)
1956 NEC
Table 1A, Page
(attached) you will note the allowance was for all single phase 3-wire edison services not just residential or even 120/240 (see the table notes for the allowance)
1956 AIEE (Became IEEE later) Paper "The Heating and Mechanical Effects of Installing Insulated Conductors in Steel Raceways" By Brandon, Kline, Geiges and Paradise. https://ieeexplore.ieee.org/document/4499473
"Purpose
The purpose of the investigation was to
compile information, observations, and
test data which could be used for analyzing
the following:
1. The applicable, current-carrying capacity
reduction factors for more than nine
conductors.
2. The effect of load diversity in reference
to the current-carrying capacity reduction
factors and conductor-operating temperatures."
This entire article is available online from IEEE, I am sending a copy of the test findings chart that illustrates the use of the term "load diversity" as not meaning the actual load being served, but the number of conductors conducting.
The chart is titled Table VIII. Diversity Tests, column titles are Wire Type, Wire Size AWG, No. of Wires, No. Conducting, Operating Temperature C, Amperes, and Volts. The first row of data is #6 AWG, 12 wires, 4 conducting, operating at 60C, 59.5Amperes and 3.5 Volts. This testing was used for our De-rating table.
The Submitter for the 17' change even shows these conductor current differences(heaters) in his attachment (attached to this input). You are allowing three heaters in an assembly instead of two, all heaters being of the same BTU output, while also eliminating the heat sink properties of the equivalence of a 0 current third conductor. The heating difference is due to three phase being 120 degrees out of phase while the edison 3 wire is 180 degrees out of phase resulting in neutral only carrying current if there is imbalance, the three phase neutral will carry 200 amps when both of the 208 legs are carrying 200 amps, it doesn't "cancel". The I^2R power loss equation shows you have three heaters compared to two equivalent, I^2R, (Current Squared X the Resistance of the Wire).
Also, If the conductors are large enough for the residential load, then the normal over-current protection device is also large enough, there is only bad reasoning to allow a larger OCPD on THE MOST SENSITIVE conductor group in the MOST VULNERABLE type of building construction. What I mean by that is service conductors only have OCPD, not upstream short circuit protection like other conductors, so if these are overloaded even just slightly just occasionally after a long period of time the result will be a fire, there's no safety left, it was eliminated with this allowance, you have no appropriate OCPD. And dwelling units are wood framed with a continual decline in fire resistance due to the materials used, houses burn much easier, faster and hotter when built out of the common materials used today compared to decades past.
If the conductors are large enough for the load then the normal OCPD is as well. I am sending a copy of common OCPD trip curves, the Square D 175Amp would take a minimum of 20.83 minutes to trip at 175 amps all the way up to 2.78 hours. At 218 amps its about 5.83 minutes to 2.78 hours. Why would a 175 amp residential service ever need to operate at 175 amps for longer than 20 minutes which is the minimum time it will take ocpd to open.
There’s well more than enough wiggle room in OCPD curves to not need this allowance, just use a smaller breaker, if the wire's big enough then the normal OCPD is as well. Also, the CEC allowance does not prove it to be safe, table 310.16 values are based on legitimate testing while the CEC allowance is not. The allowance does not mean the service will definitely result in fire it just unnecessarily removes protection, so the fact that we don't have reports of these services burning up everywhere is not a legitimate argument for fast-tracking this allowance past legitimate testing.
I will add the referenced attachments in my next posts, Thanks.