Do the downstream conductors of an ATS serving the entire load of the house qualify for 83% sizing per 310.12?
In particular I'm thinking about the sense, control, and battery charge conductors that would not be included in the feeder supplied by the ATS. In a Generac transfer switch I'm looking at, the T1, N1, and N2 conductors are protected by (3) 240VAC 6.3A fuses which makes me think I CAN'T USE THE 83% ALLOWANCE.
Rob G - Seattle
In particular I'm thinking about the sense, control, and battery charge conductors that would not be included in the feeder supplied by the ATS. In a Generac transfer switch I'm looking at, the T1, N1, and N2 conductors are protected by (3) 240VAC 6.3A fuses which makes me think I CAN'T USE THE 83% ALLOWANCE.