gfdbiker
Member
- Location
- Cincinnati, OH
My question is can you use the exception for 310.15 (a) 2 for not using the derating factor for having multiple conductors in a conduit. In my example I have a circuit length of 150' of 4 sets of 3/c 500mcm each in its' own conduit except for a distance of about six feet where it has to transition between 2 manholes and I only have 2 spare conduits (5"). Since it is less than 10' and 10% of the circuit, can I use that exception? However, 310.15 (b) 3 states that for raceways greater than 24 inches you must derate for multiple conductors. Which is the correct interpetation?