Question from one of my students. The exception reads. Where two different ampacities apply to adjacent portions of a circuit the higher ampacity shall be permitted to be used beyond the point of transition, a distance equal to 3.0 m (10ft) or 10 percent of the circuit length figured at the higher ampacity, whichever is less.
When calculating the total circuit length is the section at the an elevated temperature included in the measurement? Example - if the run is 5 feed in a area of elevated temperature and 100 ft is in an area of normal temperature, 105 ft total, do you use 100 feet or 105 feet to calculate the 10%. The exception stated at the higher ampacity, I take that as the normal temperature section, thus using the 100 ft measurement to calculate the 10%. But I am not sure I am correct on this point.
rbossler
Edited to remove the e-mail address. Please use the private messaging to exchange e-mail addresses.
[ October 04, 2004, 06:28 AM: Message edited by: charlie ]
When calculating the total circuit length is the section at the an elevated temperature included in the measurement? Example - if the run is 5 feed in a area of elevated temperature and 100 ft is in an area of normal temperature, 105 ft total, do you use 100 feet or 105 feet to calculate the 10%. The exception stated at the higher ampacity, I take that as the normal temperature section, thus using the 100 ft measurement to calculate the 10%. But I am not sure I am correct on this point.