All I have always used the 90degree column when derating for CCC's or ambient but never really remembered why. I have been going back and forth with guys at work and they seem to believe that you must use the weakest point which is typically terminations at 60 or 75. I see were it says:
"the temp correction and adjustment factors shall be permitted to be applied to the ampacity for the temperature rating of the conductor, if the corrected and adjusted ampacity does not exceed the ampacity for the temperature rating of the termination in accordance with the provisions of 110.14(C)"
But this is about as clear as mud to most. it makes sense to me up until the point they say "if" haha. I especially don't understand what they mean by saying "ampacity does not exceed the ampacity for the temperature rating". Can someone really break this paragraph down for me?
I also watched a Mike Holt Video kind of about this and he said you use 90 no matter what, basically even if you are using TW or UF which is in 60 column, you still use 90?
"the temp correction and adjustment factors shall be permitted to be applied to the ampacity for the temperature rating of the conductor, if the corrected and adjusted ampacity does not exceed the ampacity for the temperature rating of the termination in accordance with the provisions of 110.14(C)"
But this is about as clear as mud to most. it makes sense to me up until the point they say "if" haha. I especially don't understand what they mean by saying "ampacity does not exceed the ampacity for the temperature rating". Can someone really break this paragraph down for me?
I also watched a Mike Holt Video kind of about this and he said you use 90 no matter what, basically even if you are using TW or UF which is in 60 column, you still use 90?