wwhitney
- Berkeley, CA
- Retired
OK, that section seems clear enough. This is a case of the NEC text not corresponding to my understanding of the principles involved, so I'm trying to figure out which one should be adjusted.No, it is not NEC compliant to supply a 48A continuous load with #6NM cable, per 210.19(A)(1).
As I see it, the only reason that the notion of 125% of continuous loads occurs in the NEC is that standard circuit breakers are not 100% rated. That is, the circuit breaker is the weak link; everything else in the circuit is rated for continuous loads.
Therefore the checks as I would see it should be:
1) Circuit breaker rating >= 125% continuous plus noncontinuous.
2) Circuit breaker rating <= Ceiling(Wiring Ampacity) "next size up rule"
3) Wiring ampacity >= continuous plus noncontinuous.
4) Termination limitations.
The #6 NM, 48A continuous, 60A breaker example satisfies all of those. Is there a principle I'm missing, or does the language in the NEC miss this corner case?
Thanks, Wayne