Most of the time a conductor sized for 60 or 75 C will also be large enough for the overcurrent device of similar setting to the conductor ampacity. Also keep in mind we are allowed to go to the next size higher standard overcurrent device as long as the actual load doesn't exceed conductor ampacity for 800 amps and less overcurrent devices. This is a primary reason you see many 4/0 aluminum conductors (even when not applying 310.15(B)(7) allowances for dwelling services/feeders. 4/0 has an ampacity of 180 @ 75C, so as long as you don't have a load of 181 - 200 you still can protect it with a 200 amp overcurrent device. If your load is between 181 and 205 you must use at least 250 kcmil minimum conductor, but next standard size overcurrent device in that situation is 225 amps and could be used.