310.15(B)(2) and 310.16, etc

Status
Not open for further replies.

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
I know this topic has been addressed in the past...but, just to be sure:
if using 90 degree C wet/dry conductors such as THHN/THWN-2, the AMBIENT correction factors can be based on 90Degrees C, even if the termination limits the cable - such as lugs on a CB - to 75Degrees C per 110.14(C)(1)


Sent from my iPhone using Tapatalk
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
I know this topic has been addressed in the past...but, just to be sure:
if using 90 degree C wet/dry conductors such as THHN/THWN-2, the AMBIENT correction factors can be based on 90Degrees C, even if the termination limits the cable - such as lugs on a CB - to 75Degrees C per 110.14(C)(1)
Yes, that is correct.
 