mike abbott
- Ohio
NEC 310.15(B)(2) addresses the adjustment factors for more than three current carrying conductors in a conduit. However, I've run into a debate with another engineer regarding the initial ampacity of the conductor before applying the derating factor.
Take the following example: 4 current carrying #3/0 THHN in a conduit.
310.15(B)(2) requires us to derate 80%.
I believe the calculation allows for the maximum temperature rating of the wire (which is 90C for THHN). So, the calculation would be 225A X 80% = 180A.
He believes 110.14(C)(1)(b) restricts us to use the 75C column, thus the calculation would be 200A x 80% = 160A.
In either method, the overall system ampacity is still less than the 75C ampacity, so 110.14 would be satisfied.
What are your thoughts, and can you direct me to any specific code section or code examples to prove this?
Thanks!
Thanks!