310.15 (B) (21) wire ampacity

Status
Not open for further replies.

Smart $

Esteemed Member
Location
Ohio
Yes, this is over 2000 volts. However the table does not appear to list this particular multi layered type cable?
I see.

This has come up before but I forget the resolution, if any. Perhaps just look at it from the temperature limit placed on the termination [110.40]. That usually caps the ampacity anyway.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
I see.

This has come up before but I forget the resolution, if any. Perhaps just look at it from the temperature limit placed on the termination [110.40]. That usually caps the ampacity anyway.

The terminals are rated at least 90*C, but the conductor can not go over 75*C continuous as it can damage the covering.

Question for the curious. Why does 310. B 21 exist when tables 310.60 and onward technically have you covered?
 

Smart $

Esteemed Member
Location
Ohio
The terminals are rated at least 90*C, but the conductor can not go over 75*C continuous as it can damage the covering.
With the conductors being covered and the covering not recognized by Code as electrical insulation, that's a design issue.

Question for the curious. Why does 310. B 21 exist when tables 310.60 and onward technically have you covered?
Up to 2000V considerations, perhaps.

???
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
With the conductors being covered and the covering not recognized by Code as electrical insulation, that's a design issue.

I disagree (humbly), it would point me to 310.15 B 21 because it specifically says "covered"

Up to 2000V considerations, perhaps.

???


Maybe. Above 600 volts you have "bare", "covered" and "insulated"
 

Julius Right

Senior Member
Occupation
Electrical Engineer Power Station Physical Design Retired
I think you are right. NEC does not recognize the covered cable as medium voltage cable since it is not shielded as per NEC art.10(E) Shielding and not constructed as per UL1072 [indicated in Informative Annex A Product Safety Standards.]
You cannot use it as a MV cable in no way.
As indicated in Southwire catalogue:
http://www.southwire.com/ProductCatalog/XTEInterfaceServlet?contentKey=prodcatsheet85
"Used primarily for, but not limited to, overhead secondary distribution lines. Installed on insulators, otherwise treated as a bare conductor."
Ampacity may be considered as per Table 310.15(B) 21 never the less there is no indication of the covering material [pvc,xlpe,HDPE or else] and thickness, neither ANSI/ICEA S-70-547 is mentioned. The ambient is 40oC.
According to NEC the temperature is limited to 80oC and in the manufacturer catalogue only 75oC [even XLPE insulation-90oC rated- is employed] and the ambient is 25oC.
 