310.15(B)(3)(A) has the following wording:
(4) Adjustment factors shall not apply to Type AC cable or to Type MC cable under the following conditions:

[R

a. The cables do not have an overall outer jacket

Elementary, I assume, but does this apply the group of several MC cable with individual jackets as long as that group does not have an overall jacket ?
 
IMO that relates to PVC coated cables like parking deck MC.

parking-lot.png
 
I am little confused 310.15(B)(5) nec2011

I am little confused 310.15(B)(5) nec2011

what year of nec of the first question?
 

Attachments

  • 01.JPG
    01.JPG
    36.5 KB · Views: 0
It certainly reads that a standard mc cable - without the jacket- does not have to do adjustment factors. :?

It says that if it meets all of those conditions you can use the 60% correction factor. If it does not then the standard 80%, 70%, 50% bundling rules apply.
 
Got It !
Sometimes those dang trees get in the way of the forest....

One can concentrate too closely on the wording of one sentence...
 
It says that if it meets all of those conditions you can use the 60% correction factor. If it does not then the standard 80%, 70%, 50% bundling rules apply.


Yes, but I wasn't responded to what wasn't copied. Gus just thru out a part of it. He is such a trouble maker....:D
 
:happyyes: His darn thread about linear/non linear loads on a noodle just about drove me bonkers trying to find an answer.

Amazing the questions that come up when teaching a class.....
 