310.15(B)(3)(c) ROP 2011

Status
Not open for further replies.
Is this what you are looking for?

6-28 Log #99 NEC-P06
Final Action: Accept

(Table 310.15(B)(2)(c))

_______________________________________________________________

TCC Action: The Technical Correlating Committee directs that the title of Table 310.15(B)(3)(c) be changed to correlate with the action taken on Proposal 6-66 and this comment.
Submitter:
Technical Correlating Committee on National Electrical Code?,
Comment on Proposal No:
6-68
Recommendation:
It was the action of the Technical Correlating Committee that this proposal be reconsidered relative to the use of the terms ?conduit? and ?raceway? and correlated with the action taken on Proposal 6-66.
This action will be considered by the panel as a public comment.
Substantiation:
This is a direction from the National Electrical Code Technical Correlating Committee in accordance with 3.4.2 and 3.4.3 of the Regulations
Governing Committee Projects.
Panel Meeting Action: Accept
Panel Statement:
The panel?s action on Proposal 6-68 should have been to accept in principle in part. While the panel did replace ?conduits? with ?circular raceways?, the use of ?raceway? alone would include types which were not part of the submitted technical substantiation.
Number Eligible to Vote: 11
Ballot Results:
Affirmative: 11
 