bigjer
Member
- Location
- riverton ut.
would this be the neutral conductor of a 240volt single phase service?
No This is the neutral that carries the unbalanced load in a multiwire branch circuit. Thus in a single phase system where you run 2 conductors on different phases and a common neutral or a 3 phase system where you have 3 conductors on different phases and a common neutral. then the neutral conductor would not count.would this be the neutral conductor of a 240volt single phase service?
It would -- I missed the service part. I thought he was asking about something else. So we are talking parallel service conductors??? I assume.Why wouldn't this apply to service conductors?
It would -- I missed the service part. I thought he was asking about something else. So we are talking parallel service conductors??? I assume.