Re: 310.15(B)(6) - Parallel conductors
Earl
I am asking this question, because I have been asked the same question and was not sure how to answer. The handbook is a very good document, but not the formal interpretation of the NFPA. I see the handbook starts the sentence saying a single set, but I cannot see how they found that interpretation from the body of 310.15(B)(6). I am not too sure if I understand your second sentence.
As you can see, I used the amperage value of the table in .15(B)(6), and performed the conductor amperage adjustment.
Excluding the handbook, can you pick out in the NEC how they determined that it is one set?
I am not convinced that a parallel set of conductors cannot be used with the ampacity rating of the cable from table 310.15(B)(6), but... I do not know if it can
.
Do you see any impending problems if one was to install this type of arrangement?
Two sets of 4/0 copper with the ampacity adjustment using table 310.16 would equal 368 amps. Table 310.15(B)(6) permits the use of 400 kcmil for a 400 amp service, and in table 310.16 400s equals 335 amps. I do not see an amperage value problem here, so what might the problem be.
Also the jurisdiction we work in permits two sets of 4/0 aluminum SE cable, one set to each of 200 amp panel setups for a 400 amp service. Using parallel 4/0 copper would seem to be a superior installation as far as amperage is concerned.
Anyones answer(s) would be appreciated, as they may open a 'door' I am not looking in.
Pierre