newinspector1
- NC
On modular homes if mobile home feeder is used instead of ser cable does the rules of 310.15 (B)(6) still apply? Can you run other circuits to the main panel and not downsize the breaker?
It is not service, it is a sub panel fed from the panel on pole
Not following you Jim.
If he is talking about line from outside panel to inside panel it is not service
The main panel is the 1 on the pole
Maybe I am not seeing his real question
He may be worried that the feeder is not supplying the entire load.
Jim, it is just the a/c but I had the understanding that it could have no additional loads. Most people around here are just going straight to the inside panel now.
We really need to know what a mobile home feeder is. IMO, if there is pipe from the outside panel to the interior panel and the wire is rated for use in a home, not all USE cable is allowed inside, then I would say that 4/0 aluminum is okay as long as the calculated load is not more than 180 amps.
He does not have an outside panel
Mobile home feeder is typically a 3-wire with ground AL Type USE-2/RHH/RHW-2 cable, often with a smaller conductor for the neutral.We really need to know what a mobile home feeder is. IMO, if there is pipe from the outside panel to the interior panel and the wire is rated for use in a home, not all USE cable is allowed inside, then I would say that 4/0 aluminum is okay as long as the calculated load is not more than 180 amps.
Thanks and that is what I assumed. I was hoping it wasn't a URD cable. Not sure why they chose USE wire if the run is in conduit.Mobile home feeder is typically a 3-wire with ground AL Type USE-2/RHH/RHW-2 cable, often with a smaller conductor for the neutral.
http://www.cerrowire.com/default.aspx?id=38
Mike that is my question because I don't think that it is supplying the entire load. There is no pole this is a modular home with a service on the house. The electrician ran mobile home feeder and said that got him out of having to downsize his breaker.