Posts in another thread brought to mind a question that, after all these years and posts should be clear but is not.. senility I guess
I understand the 83% rule but looking at 310.15(B)7)(3) and the fact that it refers back to (1)&(2) does (7) mean that in no case shall the feeder be required to be larger than the service OR only when the "entire load" is still in play.
Assume a 200 amp residential service where I take advantage of the 83% rule. I add a 20 amp or 40 amp 240v load at the service panel. The feeder no longer carries the "entire load" and I have lost my load diversity. Can I still run a feeder the same size as the service based on (B)(7)(3) or not ??
I understand the 83% rule but looking at 310.15(B)7)(3) and the fact that it refers back to (1)&(2) does (7) mean that in no case shall the feeder be required to be larger than the service OR only when the "entire load" is still in play.
Assume a 200 amp residential service where I take advantage of the 83% rule. I add a 20 amp or 40 amp 240v load at the service panel. The feeder no longer carries the "entire load" and I have lost my load diversity. Can I still run a feeder the same size as the service based on (B)(7)(3) or not ??