dm9289
Industrial Maintenance Electrician
- Location
- Pennsylvania
- Occupation
- Industrial process repair/ maintenance Electrician
Lets say multiple dwelling unit. 3 units calculated load 80 amps each so 240 amps all 3 combined.
So I'm assuming the service conductor size must be capable of 240 amps so 350kcm aluminum at 75C at 250 amps. I think what code says is i cant use 83% rule
do you agree?
So for main feed for all 3- 310.15(B)(7) rules do not apply?
All 3 units even though the calculated load is 80amp minimum service size is 100amps so for these individual dwelling unit feeders should be based on 100amp OCP not 80 amp calculated load but can be done at 83% of 100amp due to 310.15(B)(7) so 83 amps so #2 aluminum at 90amps.
Is this correct application of this section?
So I'm assuming the service conductor size must be capable of 240 amps so 350kcm aluminum at 75C at 250 amps. I think what code says is i cant use 83% rule
do you agree?
So for main feed for all 3- 310.15(B)(7) rules do not apply?
All 3 units even though the calculated load is 80amp minimum service size is 100amps so for these individual dwelling unit feeders should be based on 100amp OCP not 80 amp calculated load but can be done at 83% of 100amp due to 310.15(B)(7) so 83 amps so #2 aluminum at 90amps.
Is this correct application of this section?